Spoke with my electrician today,your right 240v is now 220v just like 3 phase 415v to 400v
PeeBee is quite right, nominal voltage was changed from 240V to 230V to comply with Europe but in practice nothing really changed because we are within the +10% allowance. So although voltage is stated as 230V the average actual voltage is still around 240V. The difference in current draw between 220V and 240V for a 5.5kW element is only 2 amps or so and a 25 amp supply should be fine.